Part 6 - Inspection and Testing
Study guide for BS 7671 Part 6 covering initial verification, periodic inspection, the correct testing sequence, and certification requirements including EIC, MEIWC, and EICR documentation.
Key Areas Covered
Overview
Part 6 of BS 7671 sets out the requirements for the inspection and testing of electrical installations, both at initial verification upon completion of new work and at periodic intervals throughout the life of an installation. With an exam weighting of 7%, this topic is moderately weighted but consistently produces questions that candidates find challenging.
The critical concept in Part 6 is that every installation must be verified as compliant before being put into service. This verification comprises a detailed visual inspection followed by a defined sequence of tests. The order of these tests is not arbitrary — it is specified to ensure that each test builds upon the results of the preceding one and that safety is maintained throughout the testing process.
In this guide:
Key Sections
Chapter 61 - Initial Verification (Regulations 610-622)
Initial verification must be carried out on every:
- New installation
- Addition to an existing installation
- Alteration to an existing installation
…before it is put into service.
Visual Inspection (Regulation 611)
A detailed visual inspection must be carried out before testing begins and, where practicable, with the installation de-energised. The inspection must confirm:
| Check | What to Verify |
|---|---|
| Selection and erection | Correct selection and erection of equipment |
| Accessibility | Adequate accessibility for operation and maintenance |
| Labelling | Correct labelling and identification of circuits |
| Connections | Appropriate connection of conductors |
| Fire protection | Presence of fire barriers, seals, and protective devices |
| Environmental suitability | Suitability of equipment for the environmental conditions |
Testing Sequence (Regulation 612)
The testing sequence for initial verification must be followed in order because each test may depend on the satisfactory results of previous tests:
| Step | Test | Regulation |
|---|---|---|
| 1 | Continuity of protective conductors (including main and supplementary bonding) | 612.2 |
| 2 | Continuity of ring final circuit conductors | 612.2 |
| 3 | Insulation resistance | 612.3 |
| 4 | SELV and PELV verification (where applicable) | 612.4 |
| 5 | Polarity | 612.6 |
| 6 | Earth electrode resistance (for TT systems) | 612.7 |
| 7 | Earth fault loop impedance | 612.9 |
| 8 | Additional protection (RCD testing) | 612.10 |
| 9 | Prospective fault current | 612.11 |
| 10 | Check of phase sequence (for multi-phase circuits) | 612.12 |
| 11 | Functional testing | 612.13 |
| 12 | Voltage drop (where required by measurement) | 612.14 |
Exam tip: The testing sequence in Regulation 612 is tested in almost every exam sitting. Memorise the order: Continuity → Continuity (ring) → Insulation → SELV/PELV → Polarity → Earth electrode → Loop impedance → RCD → Prospective fault current → Phase sequence → Functional → Voltage drop.
Insulation Resistance Test Values (Regulation 612.3)
| Circuit Voltage | Test Voltage | Minimum Resistance |
|---|---|---|
| SELV and PELV | 250V DC | ≥ 1.0 MΩ |
| Up to and including 500V | 500V DC | ≥ 1.0 MΩ |
| Above 500V | 1000V DC | ≥ 0.5 MΩ |
The 500V DC test voltage yielding a minimum of 1.0 MΩ for standard circuits is one of the most commonly tested figures in the exam.
Chapter 62 - Periodic Inspection and Testing (Regulation 631)
Every installation must be subject to periodic inspection and testing at intervals determined by:
| Factor | Detail |
|---|---|
| Type | The type of installation |
| Use and occupancy | How the installation is used and occupied |
| External influences | Environmental conditions to which it is subjected |
| Condition | The current condition of the installation |
Recommended Inspection Intervals
| Installation Type | Recommended Interval |
|---|---|
| Domestic | Every 10 years (or on change of occupancy) |
| Commercial | Every 5 years |
| Industrial | Every 3 years |
| Swimming pools | Annually |
| Construction sites | Every 3 months |
| Caravan parks | Annually |
During periodic inspection, it is not always necessary to carry out every test in the initial verification sequence. The scope of testing is determined by the inspector based on available records and the condition observed during visual inspection.
Important: These intervals are recommendations, not mandatory fixed periods. The decision on frequency is based on the type, use, and condition of the installation.
Chapters 63-65 - Certification and Reporting (Regulations 641-651)
Upon completion of verification, the appropriate certification must be issued. There are three principal forms:
Electrical Installation Certificate (EIC) — Regulation 641
- Required for all new installations
- Certifies that the installation complies with BS 7671
- Must be signed by three responsible persons:
| Role | Responsibility |
|---|---|
| Designer | Certifies the design complies with BS 7671 |
| Installer | Certifies the installation was erected in accordance with the design |
| Inspector | Certifies the installation has been inspected and tested (may be the same person for smaller installations) |
Minor Electrical Installation Works Certificate (MEIWC)
Issued for minor works such as:
- Adding a socket outlet to an existing circuit
- Replacing a consumer unit where the circuit design is unaffected
- Adding a lighting point to an existing circuit
Electrical Installation Condition Report (EICR) — Regulation 651
Issued following periodic inspection and testing. It records the condition of the existing installation using a coding system to classify deficiencies:
| Code | Meaning | Action Required |
|---|---|---|
| C1 | Danger present | Immediate remedial action required |
| C2 | Potentially dangerous | Urgent remedial action required |
| C3 | Improvement recommended | Advisory — no immediate action |
| FI | Further investigation required | Cannot be fully assessed without further work |
Important Regulation Numbers
| Regulation | Requirement |
|---|---|
| 611 | Visual inspection requirements (before testing, supply de-energised) |
| 612 | Testing sequence for initial verification |
| 612.2 | Continuity of protective conductors and ring final circuits |
| 612.3 | Insulation resistance testing (minimum 1.0 MΩ at 500V DC) |
| 612.6 | Polarity verification |
| 612.9 | Earth fault loop impedance measurement |
| 612.10 | RCD testing (additional protection verification) |
| 621-622 | Initial verification procedures and requirements |
| 631 | Periodic inspection and testing |
| 641 | Electrical Installation Certificate (EIC) requirements |
| 651 | Electrical Installation Condition Report (EICR) requirements |
Common Exam Topics
- The correct testing sequence as defined in Regulation 612 (tested in almost every exam sitting)
- Minimum insulation resistance values and the corresponding test voltages
- When to issue an EIC versus a MEIWC versus an EICR
- The EICR condition coding system (C1, C2, C3, FI) and what each code means
- Whether visual inspection comes before or after testing (always before)
- Recommended periodic inspection intervals for different installation types
- Who must sign an Electrical Installation Certificate
- Earth fault loop impedance testing and its relationship to disconnection times in Part 4
Study Tips
- Memorise the testing sequence in Regulation 612. A useful mnemonic for the first tests is: “Continuity, Continuity (ring), Insulation, SELV/PELV, Polarity, Earth electrode, Loop impedance, RCD.” Questions frequently ask what comes before or after a specific test.
- Know the insulation resistance minimum values and test voltages as a pair: 500V test voltage → minimum 1.0 MΩ for most standard circuits.
- Understand the difference between the three certificate types. A common exam question describes a scenario and asks which certificate is appropriate.
- Link the earth fault loop impedance test back to the disconnection times in Regulation 411.3.2 (Part 4). The measured Zs must be low enough to ensure the protective device disconnects within the required time.
- Remember that periodic inspection intervals are recommendations, not mandatory fixed periods.
Related Topics
Practice Questions: Part 6 - Inspection and Testing
Test your knowledge with 14 free practice questions. Get all 28 questions in the app.
Question 1 of 14
Part 6 - Inspection and Testing
Quiz Complete!
0
Correct
0
Incorrect
0%
Score
Get your results emailed to you
Results sent! Check your inbox.
Related Articles
Continuity of Protective Conductors: The Essential R1+R2 Test Explained
A practical guide to CPC continuity testing per BS 7671. Covers the R1+R2 method, the wander lead method, expected values, what the results tell you, and why this is the first test in the sequence.
Insulation Resistance Testing: Why We Do It, How to Do It, and Common Problems
A complete guide to insulation resistance (IR) testing per BS 7671. Covers test voltages, minimum values, the neutral conductor problem, false positives and negatives, and practical troubleshooting for the IET exam.
R1+R2 Ring Final Circuit Test: Why Your Values Don't Match
Getting unequal R1+R2 readings when testing a ring final circuit? Learn the 3-step test procedure, the expected values, and the 5 most common reasons your readings don't match — with diagrams.