Part 6 - Inspection and Testing

Study guide for BS 7671 Part 6 covering initial verification, periodic inspection, the correct testing sequence, and certification requirements including EIC, MEIWC, and EICR documentation.

Regulations 610-651 ~4% of exam 14 free questions

Key Areas Covered

Initial verificationPeriodic inspectionTesting sequenceDocumentation requirementsCertification

Overview

Part 6 of BS 7671 sets out the requirements for the inspection and testing of electrical installations, both at initial verification upon completion of new work and at periodic intervals throughout the life of an installation. With an exam weighting of 7%, this topic is moderately weighted but consistently produces questions that candidates find challenging.

The critical concept in Part 6 is that every installation must be verified as compliant before being put into service. This verification comprises a detailed visual inspection followed by a defined sequence of tests. The order of these tests is not arbitrary — it is specified to ensure that each test builds upon the results of the preceding one and that safety is maintained throughout the testing process.

Key Sections

Chapter 61 - Initial Verification (Regulations 610-622)

Initial verification must be carried out on every:

  • New installation
  • Addition to an existing installation
  • Alteration to an existing installation

…before it is put into service.

Visual Inspection (Regulation 611)

A detailed visual inspection must be carried out before testing begins and, where practicable, with the installation de-energised. The inspection must confirm:

CheckWhat to Verify
Selection and erectionCorrect selection and erection of equipment
AccessibilityAdequate accessibility for operation and maintenance
LabellingCorrect labelling and identification of circuits
ConnectionsAppropriate connection of conductors
Fire protectionPresence of fire barriers, seals, and protective devices
Environmental suitabilitySuitability of equipment for the environmental conditions

Testing Sequence (Regulation 612)

The testing sequence for initial verification must be followed in order because each test may depend on the satisfactory results of previous tests:

StepTestRegulation
1Continuity of protective conductors (including main and supplementary bonding)612.2
2Continuity of ring final circuit conductors612.2
3Insulation resistance612.3
4SELV and PELV verification (where applicable)612.4
5Polarity612.6
6Earth electrode resistance (for TT systems)612.7
7Earth fault loop impedance612.9
8Additional protection (RCD testing)612.10
9Prospective fault current612.11
10Check of phase sequence (for multi-phase circuits)612.12
11Functional testing612.13
12Voltage drop (where required by measurement)612.14

Exam tip: The testing sequence in Regulation 612 is tested in almost every exam sitting. Memorise the order: Continuity → Continuity (ring) → Insulation → SELV/PELV → Polarity → Earth electrode → Loop impedance → RCD → Prospective fault current → Phase sequence → Functional → Voltage drop.

Insulation Resistance Test Values (Regulation 612.3)

Circuit VoltageTest VoltageMinimum Resistance
SELV and PELV250V DC≥ 1.0 MΩ
Up to and including 500V500V DC≥ 1.0 MΩ
Above 500V1000V DC≥ 0.5 MΩ

The 500V DC test voltage yielding a minimum of 1.0 MΩ for standard circuits is one of the most commonly tested figures in the exam.

Chapter 62 - Periodic Inspection and Testing (Regulation 631)

Every installation must be subject to periodic inspection and testing at intervals determined by:

FactorDetail
TypeThe type of installation
Use and occupancyHow the installation is used and occupied
External influencesEnvironmental conditions to which it is subjected
ConditionThe current condition of the installation
Installation TypeRecommended Interval
DomesticEvery 10 years (or on change of occupancy)
CommercialEvery 5 years
IndustrialEvery 3 years
Swimming poolsAnnually
Construction sitesEvery 3 months
Caravan parksAnnually

During periodic inspection, it is not always necessary to carry out every test in the initial verification sequence. The scope of testing is determined by the inspector based on available records and the condition observed during visual inspection.

Important: These intervals are recommendations, not mandatory fixed periods. The decision on frequency is based on the type, use, and condition of the installation.

Chapters 63-65 - Certification and Reporting (Regulations 641-651)

Upon completion of verification, the appropriate certification must be issued. There are three principal forms:

Electrical Installation Certificate (EIC) — Regulation 641

  • Required for all new installations
  • Certifies that the installation complies with BS 7671
  • Must be signed by three responsible persons:
RoleResponsibility
DesignerCertifies the design complies with BS 7671
InstallerCertifies the installation was erected in accordance with the design
InspectorCertifies the installation has been inspected and tested (may be the same person for smaller installations)

Minor Electrical Installation Works Certificate (MEIWC)

Issued for minor works such as:

  • Adding a socket outlet to an existing circuit
  • Replacing a consumer unit where the circuit design is unaffected
  • Adding a lighting point to an existing circuit

Electrical Installation Condition Report (EICR) — Regulation 651

Issued following periodic inspection and testing. It records the condition of the existing installation using a coding system to classify deficiencies:

CodeMeaningAction Required
C1Danger presentImmediate remedial action required
C2Potentially dangerousUrgent remedial action required
C3Improvement recommendedAdvisory — no immediate action
FIFurther investigation requiredCannot be fully assessed without further work

Important Regulation Numbers

RegulationRequirement
611Visual inspection requirements (before testing, supply de-energised)
612Testing sequence for initial verification
612.2Continuity of protective conductors and ring final circuits
612.3Insulation resistance testing (minimum 1.0 MΩ at 500V DC)
612.6Polarity verification
612.9Earth fault loop impedance measurement
612.10RCD testing (additional protection verification)
621-622Initial verification procedures and requirements
631Periodic inspection and testing
641Electrical Installation Certificate (EIC) requirements
651Electrical Installation Condition Report (EICR) requirements

Common Exam Topics

  • The correct testing sequence as defined in Regulation 612 (tested in almost every exam sitting)
  • Minimum insulation resistance values and the corresponding test voltages
  • When to issue an EIC versus a MEIWC versus an EICR
  • The EICR condition coding system (C1, C2, C3, FI) and what each code means
  • Whether visual inspection comes before or after testing (always before)
  • Recommended periodic inspection intervals for different installation types
  • Who must sign an Electrical Installation Certificate
  • Earth fault loop impedance testing and its relationship to disconnection times in Part 4

Study Tips

  • Memorise the testing sequence in Regulation 612. A useful mnemonic for the first tests is: “Continuity, Continuity (ring), Insulation, SELV/PELV, Polarity, Earth electrode, Loop impedance, RCD.” Questions frequently ask what comes before or after a specific test.
  • Know the insulation resistance minimum values and test voltages as a pair: 500V test voltage → minimum 1.0 MΩ for most standard circuits.
  • Understand the difference between the three certificate types. A common exam question describes a scenario and asks which certificate is appropriate.
  • Link the earth fault loop impedance test back to the disconnection times in Regulation 411.3.2 (Part 4). The measured Zs must be low enough to ensure the protective device disconnects within the required time.
  • Remember that periodic inspection intervals are recommendations, not mandatory fixed periods.

Practice Questions: Part 6 - Inspection and Testing

Test your knowledge with 14 free practice questions. Get all 28 questions in the app.

Question 1 of 14

Part 6 - Inspection and Testing

0 / 0

Want the complete study experience?

Get 28 questions on this topic plus mock tests, progress tracking, and offline access.