Part 5 - Selection and Erection of Equipment

Study guide for BS 7671 Part 5 covering cable selection and sizing, wiring systems, earthing arrangements, switchgear, and isolation requirements. The highest-weighted exam topic at 14%.

Regulations 510-559 ~14% of exam 28 free questions

Key Areas Covered

Common rules for equipment selectionWiring systemsSwitchgear and controlgearEarthing arrangementsCable selection and sizingIsolation and switching

Overview

Part 5 of BS 7671 is the largest and most practically focused section of the Wiring Regulations, dealing with the selection and erection of all electrical equipment within an installation. With an exam weighting of 14%, it carries the highest number of questions of any topic area and demands thorough preparation.

This part translates the protective principles set out in Part 4 into concrete requirements for choosing cables, wiring systems, switchgear, earthing conductors, and switching devices. Candidates must understand not only the individual rules but also how they interact — cable selection, for example, requires simultaneous consideration of current-carrying capacity, voltage drop, fault current withstand, grouping factors, and thermal insulation.

Key Sections

Chapter 51 - Common Rules (Regulations 510-515)

Chapter 51 establishes the overarching principles for selecting all equipment:

PrincipleDetail
Comply with applicable product standardsAll equipment must meet relevant British or European standards
Voltage, current, and frequencyEquipment must be selected and erected for the electrical characteristics of the installation
Suitable for external influencesEvery item must withstand the environmental conditions it will encounter

Regulation 512 requires suitability for the conditions of the location, including:

External InfluenceExample
Ambient temperatureHigh or low temperature environments
Presence of waterIPX ratings for moisture and submersion
Mechanical impactVibration, physical damage risks
Corrosive or polluting substancesChemical exposure, salt air
Flora, fauna, and electromagnetic influencesBiological growth, vermin, EMI

The external influences classification system (Appendix 5) is referenced frequently in exam questions.

Chapter 52 - Wiring Systems (Regulations 521-529)

This chapter covers the selection and installation of wiring systems. It is one of the most detail-rich areas of the exam.

Cable Types and Installation Methods (Regulation 521)

The type of wiring system is selected based on the nature of the location and external influences. Common systems include:

SystemDescription
Cables in conduitMetallic or non-metallic
Cables in trunkingMetallic or non-metallic
Cables on cable tray or cable ladderOpen support systems
Steel wire armoured (SWA) cablesMechanically protected cables
Thermoplastic (PVC) and thermosetting (XLPE)Insulated cable types

Cable Current-Carrying Capacity (Regulation 523)

The tabulated current-carrying capacity must satisfy the relationship:

It ≥ In / (Ca × Cg × Ci × Cc)

Where the correction factors are:

FactorWhat It Corrects For
CaAmbient temperature
CgGrouping (cables installed together)
CiThermal insulation
CcType of protective device

The actual current-carrying capacity values are found in the tables in Appendix 4.

Voltage Drop Limits (Regulation 525)

Key values: Voltage drop must not exceed 3% for lighting circuits and 5% for all other circuits.

These percentage figures are among the most commonly tested values in the exam. The total drop from the origin of the installation must not exceed the values specified in Appendix 12.

Other Key Requirements

  • Regulation 526 — All electrical connections must be accessible for inspection, testing, and maintenance (unless specifically designed to be buried, such as underground cable joints)
  • Regulation 527 — Cables must be selected and erected to minimise the spread of fire, including fire-stopping and sealing where cables pass through fire barriers

Chapter 53 - Switchgear and Controlgear (Regulation 530)

Switchgear must be selected with regard to:

  • Its duty (making and breaking capacity)
  • The conditions of its location
  • The prospective fault current at the point of installation

The making and breaking capacity links directly to the overcurrent protection requirements of Part 4, Chapter 43.

Chapter 54 - Earthing Arrangements and Protective Conductors (Regulations 541-544)

This chapter sets out the requirements for all protective conductors. It contains some of the most frequently tested tables in the exam.

Circuit Protective Conductor (CPC) Sizing — Table 54.7

Line Conductor SizeMinimum CPC Size
Up to 16mm²Equal to the line conductor
16mm² to 35mm²16mm²
Above 35mm²Half the line conductor size

Main Protective Bonding Conductors (Regulation 544.1)

Minimum sizes for main protective bonding conductors:

RequirementValue
Minimum copper6mm² (or 10mm² aluminium)
Relative to earthing conductorNot less than half the cross-sectional area
Maximum for copper25mm²

Supplementary Bonding Conductors

Where required, supplementary bonding conductors must be:

ConditionMinimum Size
Mechanically protected4mm² copper
Not mechanically protected2.5mm²

Chapter 55 - Other Equipment (Regulations 551-559)

This chapter addresses specific types of equipment:

  • Section 551 — Generators and low-voltage generating sets
  • Section 559 — Luminaires and lighting installations (particularly relevant for emergency lighting questions)
  • Safety services and standby supply requirements

Important Regulation Numbers

RegulationRequirement
512Equipment suitability for external influences
521-522Selection and erection of wiring systems; external influences on cables
523Current-carrying capacities of cables (references Appendix 4)
525Voltage drop limits (3% lighting, 5% other)
526Electrical connections (accessibility requirements)
527Minimising spread of fire
530Switchgear selection and breaking capacity
541-543Earthing arrangements and earthing conductors
544.1Main protective bonding conductor sizing (minimum 6mm² Cu)
Table 54.7Minimum cross-sectional area of protective conductors
559Luminaires and lighting installations

Common Exam Topics

  • Cable sizing calculations using correction factors (Ca, Cg, Ci, Cc) and Appendix 4 tables
  • Voltage drop calculations and the 3%/5% limits
  • Protective conductor sizing using Table 54.7
  • Main protective bonding conductor minimum sizes
  • External influences classification and its effect on equipment selection
  • IP ratings and their meaning for enclosure protection
  • Wiring system selection for different environments (conduit, trunking, SWA)
  • Requirements for accessibility of connections (Regulation 526)
  • Fire-stopping requirements where cables penetrate fire barriers

Study Tips

  • Table 54.7 is essential to memorise. The three size bands (up to 16mm², 16-35mm², above 35mm²) and corresponding CPC requirements appear in multiple exam questions.
  • Practice voltage drop calculations using Appendix 4 data. Know the formula: voltage drop = mV/A/m × design current × route length / 1000.
  • Understand how to apply multiple correction factors to determine the required tabulated current rating. Work through several cable sizing examples to build confidence.
  • Remember the bonding conductor minimums: 6mm² copper, 10mm² aluminium. These are frequently tested.
  • Link Part 5 requirements back to Part 4 principles. For instance, the selection of an overcurrent device in Chapter 53 must satisfy the coordination rules in Chapter 43.

Practice Questions: Part 5 - Selection and Erection of Equipment

Test your knowledge with 28 free practice questions. Get all 130 questions in the app.

Question 1 of 28

Part 5 - Selection and Erection of Equipment

0 / 0

Want the complete study experience?

Get 130 questions on this topic plus mock tests, progress tracking, and offline access.