Part 5 - Selection and Erection of Equipment
Study guide for BS 7671 Part 5 covering cable selection and sizing, wiring systems, earthing arrangements, switchgear, and isolation requirements. The highest-weighted exam topic at 14%.
Key Areas Covered
Overview
Part 5 of BS 7671 is the largest and most practically focused section of the Wiring Regulations, dealing with the selection and erection of all electrical equipment within an installation. With an exam weighting of 14%, it carries the highest number of questions of any topic area and demands thorough preparation.
This part translates the protective principles set out in Part 4 into concrete requirements for choosing cables, wiring systems, switchgear, earthing conductors, and switching devices. Candidates must understand not only the individual rules but also how they interact — cable selection, for example, requires simultaneous consideration of current-carrying capacity, voltage drop, fault current withstand, grouping factors, and thermal insulation.
In this guide:
Key Sections
Chapter 51 - Common Rules (Regulations 510-515)
Chapter 51 establishes the overarching principles for selecting all equipment:
| Principle | Detail |
|---|---|
| Comply with applicable product standards | All equipment must meet relevant British or European standards |
| Voltage, current, and frequency | Equipment must be selected and erected for the electrical characteristics of the installation |
| Suitable for external influences | Every item must withstand the environmental conditions it will encounter |
Regulation 512 requires suitability for the conditions of the location, including:
| External Influence | Example |
|---|---|
| Ambient temperature | High or low temperature environments |
| Presence of water | IPX ratings for moisture and submersion |
| Mechanical impact | Vibration, physical damage risks |
| Corrosive or polluting substances | Chemical exposure, salt air |
| Flora, fauna, and electromagnetic influences | Biological growth, vermin, EMI |
The external influences classification system (Appendix 5) is referenced frequently in exam questions.
Chapter 52 - Wiring Systems (Regulations 521-529)
This chapter covers the selection and installation of wiring systems. It is one of the most detail-rich areas of the exam.
Cable Types and Installation Methods (Regulation 521)
The type of wiring system is selected based on the nature of the location and external influences. Common systems include:
| System | Description |
|---|---|
| Cables in conduit | Metallic or non-metallic |
| Cables in trunking | Metallic or non-metallic |
| Cables on cable tray or cable ladder | Open support systems |
| Steel wire armoured (SWA) cables | Mechanically protected cables |
| Thermoplastic (PVC) and thermosetting (XLPE) | Insulated cable types |
Cable Current-Carrying Capacity (Regulation 523)
The tabulated current-carrying capacity must satisfy the relationship:
It ≥ In / (Ca × Cg × Ci × Cc)
Where the correction factors are:
| Factor | What It Corrects For |
|---|---|
| Ca | Ambient temperature |
| Cg | Grouping (cables installed together) |
| Ci | Thermal insulation |
| Cc | Type of protective device |
The actual current-carrying capacity values are found in the tables in Appendix 4.
Voltage Drop Limits (Regulation 525)
Key values: Voltage drop must not exceed 3% for lighting circuits and 5% for all other circuits.
These percentage figures are among the most commonly tested values in the exam. The total drop from the origin of the installation must not exceed the values specified in Appendix 12.
Other Key Requirements
- Regulation 526 — All electrical connections must be accessible for inspection, testing, and maintenance (unless specifically designed to be buried, such as underground cable joints)
- Regulation 527 — Cables must be selected and erected to minimise the spread of fire, including fire-stopping and sealing where cables pass through fire barriers
Chapter 53 - Switchgear and Controlgear (Regulation 530)
Switchgear must be selected with regard to:
- Its duty (making and breaking capacity)
- The conditions of its location
- The prospective fault current at the point of installation
The making and breaking capacity links directly to the overcurrent protection requirements of Part 4, Chapter 43.
Chapter 54 - Earthing Arrangements and Protective Conductors (Regulations 541-544)
This chapter sets out the requirements for all protective conductors. It contains some of the most frequently tested tables in the exam.
Circuit Protective Conductor (CPC) Sizing — Table 54.7
| Line Conductor Size | Minimum CPC Size |
|---|---|
| Up to 16mm² | Equal to the line conductor |
| 16mm² to 35mm² | 16mm² |
| Above 35mm² | Half the line conductor size |
Main Protective Bonding Conductors (Regulation 544.1)
Minimum sizes for main protective bonding conductors:
| Requirement | Value |
|---|---|
| Minimum copper | 6mm² (or 10mm² aluminium) |
| Relative to earthing conductor | Not less than half the cross-sectional area |
| Maximum for copper | 25mm² |
Supplementary Bonding Conductors
Where required, supplementary bonding conductors must be:
| Condition | Minimum Size |
|---|---|
| Mechanically protected | 4mm² copper |
| Not mechanically protected | 2.5mm² |
Chapter 55 - Other Equipment (Regulations 551-559)
This chapter addresses specific types of equipment:
- Section 551 — Generators and low-voltage generating sets
- Section 559 — Luminaires and lighting installations (particularly relevant for emergency lighting questions)
- Safety services and standby supply requirements
Important Regulation Numbers
| Regulation | Requirement |
|---|---|
| 512 | Equipment suitability for external influences |
| 521-522 | Selection and erection of wiring systems; external influences on cables |
| 523 | Current-carrying capacities of cables (references Appendix 4) |
| 525 | Voltage drop limits (3% lighting, 5% other) |
| 526 | Electrical connections (accessibility requirements) |
| 527 | Minimising spread of fire |
| 530 | Switchgear selection and breaking capacity |
| 541-543 | Earthing arrangements and earthing conductors |
| 544.1 | Main protective bonding conductor sizing (minimum 6mm² Cu) |
| Table 54.7 | Minimum cross-sectional area of protective conductors |
| 559 | Luminaires and lighting installations |
Common Exam Topics
- Cable sizing calculations using correction factors (Ca, Cg, Ci, Cc) and Appendix 4 tables
- Voltage drop calculations and the 3%/5% limits
- Protective conductor sizing using Table 54.7
- Main protective bonding conductor minimum sizes
- External influences classification and its effect on equipment selection
- IP ratings and their meaning for enclosure protection
- Wiring system selection for different environments (conduit, trunking, SWA)
- Requirements for accessibility of connections (Regulation 526)
- Fire-stopping requirements where cables penetrate fire barriers
Study Tips
- Table 54.7 is essential to memorise. The three size bands (up to 16mm², 16-35mm², above 35mm²) and corresponding CPC requirements appear in multiple exam questions.
- Practice voltage drop calculations using Appendix 4 data. Know the formula: voltage drop = mV/A/m × design current × route length / 1000.
- Understand how to apply multiple correction factors to determine the required tabulated current rating. Work through several cable sizing examples to build confidence.
- Remember the bonding conductor minimums: 6mm² copper, 10mm² aluminium. These are frequently tested.
- Link Part 5 requirements back to Part 4 principles. For instance, the selection of an overcurrent device in Chapter 53 must satisfy the coordination rules in Chapter 43.
Related Topics
Practice Questions: Part 5 - Selection and Erection of Equipment
Test your knowledge with 28 free practice questions. Get all 130 questions in the app.
Question 1 of 28
Part 5 - Selection and Erection of Equipment
Quiz Complete!
0
Correct
0
Incorrect
0%
Score
Get your results emailed to you
Results sent! Check your inbox.
Related Articles
The Adiabatic Equation Explained: How to Check if Your CPC Is Big Enough
A clear explanation of the adiabatic equation S = √(I²t) ÷ k from BS 7671. Learn what it does, when to use it, and how to work through the calculation with a step-by-step example for the IET exam.
The Dangers of a Shared (Borrowed) Neutral: Why Every Circuit Needs Its Own
Understand why shared neutral conductors are dangerous and prohibited by BS 7671. Covers the risks of overloading, broken neutrals, RCD incompatibility, and safe isolation failures — with diagrams for the IET exam.
Two-Way and Intermediate Switching: How It Works and How to Wire It
A clear guide to two-way and intermediate lighting switching for the IET exam. Covers how 2-way switches work, strappers, intermediate cross-over switches, terminal markings, wiring diagrams, and common faults.