Part 7 - Special Installations or Locations
Study guide for Part 7 of BS 7671 — special locations including bathrooms, swimming pools, construction sites, agricultural premises, solar PV, and EV.
Key Areas Covered
Overview
Part 7 of BS 7671 addresses locations and installations where the risk of electric shock or fire is increased beyond that encountered in ordinary installations. Each section identifies a specific type of location and sets out additional or modified requirements that must be applied on top of the general rules found in Parts 1 through 6.
The underlying principle is that certain environments present heightened hazards due to factors such as:
- The presence of water
- Reduced body resistance
- Contact with Earth potential
- The involvement of vulnerable people or animals
Key principle: Part 7 does not replace the general requirements — it supplements them. When designing or inspecting a special location, the electrician must first satisfy all relevant general rules and then apply the additional Part 7 requirements specific to that location.
This part carries a significant exam weighting because it spans many distinct sections, each with its own set of rules, zone definitions, IP ratings, and protective measures.
In this guide:
Key Sections
Section 701 - Locations Containing a Bath or Shower
Section 701 is one of the most frequently examined areas within Part 7. It divides the bathroom into three zones, each with specific requirements.
Zone Definitions
| Zone | Description | IP Rating Required |
|---|---|---|
| Zone 0 | Inside the bath tub or shower basin | IPX7 (immersion protection) |
| Zone 1 | Above Zone 0, up to 2.25m from finished floor level | IPX4 (or IPX5 where water jets are used) |
| Zone 2 | Extending 0.6m horizontally beyond Zone 1 | IPX4 |
Key Requirements
| Requirement | Detail |
|---|---|
| RCD protection | All circuits serving the location must be protected by a 30mA RCD |
| SELV in Zone 0 | Only SELV at a maximum of 12V AC or 30V DC is permitted |
| Socket outlets | Not permitted in Zones 0, 1, or 2 (except shaver sockets to BS EN 61558-2-5) |
| Supplementary bonding | May be omitted where all circuits comply with the conditions in Regulation 701.415.2 |
Section 702 - Swimming Pools and Other Basins
Swimming pools present extreme risk due to full body immersion and close contact with earthed surfaces.
Zone Definitions
| Zone | Description |
|---|---|
| Zone 0 | Interior of the pool basin |
| Zone 1 | Up to 2m horizontally from the pool edge and 2.5m above the floor |
| Zone 2 | A further 1.5m horizontally beyond Zone 1 |
Key Requirements
- Only SELV not exceeding 12V AC is permitted in Zone 0
- Electrical equipment in Zones 0 and 1 must meet stringent IP ratings
- Socket outlets are generally not permitted within Zone 1
- All metalwork must be connected to supplementary bonding
Section 704 - Construction and Demolition Site Installations
Construction sites require robust temporary supplies designed for harsh conditions.
Key requirements:
| Requirement | Detail |
|---|---|
| Reduced low voltage | 110V centre-tapped to earth is the standard for portable hand tools, giving 55V to earth |
| RCD (up to 32A) | Socket outlets rated up to 32A must have 30mA RCD protection |
| RCD (above 32A) | Socket outlets rated above 32A require 500mA RCD protection |
| Mechanical protection | Supplies must withstand harsh mechanical and environmental conditions |
| Periodic inspection | Recommended every 3 months |
Section 705 - Agricultural and Horticultural Premises
Agricultural environments involve livestock, which are more susceptible to electric shock than humans.
Key requirements:
| Requirement | Detail |
|---|---|
| Touch voltage limits | Reduced compared to standard installations |
| Supplementary bonding | Required in locations accessible to livestock |
| RCD protection | All socket outlet circuits up to 32A must have 30mA RCD protection |
| Fire-risk locations | Barns storing hay and similar locations require additional consideration of thermal effects |
| Cable protection | Cables must be protected against rodent damage and mechanical impact |
Section 712 - Solar Photovoltaic (PV) Supply Systems
Section 712 addresses the installation of PV arrays and their connection to the electrical installation.
Key requirements:
| Requirement | Detail |
|---|---|
| DC isolation | Appropriate DC isolation must be provided |
| Warning labels | Must be placed at the main distribution board, the meter position, and any point where the PV supply can be isolated |
| Fault current protection | String and array cables must be adequately protected against fault currents |
| Cable suitability | Cables must be suitable for the environmental conditions on rooftops (UV exposure, temperature extremes) |
Important: PV arrays cannot be switched off while exposed to light. This creates unique hazards for installers and maintenance personnel.
Section 722 - Electric Vehicle Charging Installations
Section 722 covers the supply of electricity to electric vehicles.
Key requirements:
| Requirement | Detail |
|---|---|
| Individual circuit | Each charging point must be supplied by its own dedicated circuit |
| Minimum RCD protection | 30mA Type A RCD required |
| Type B RCD | May be required where DC fault current could arise, unless the charger has built-in DC fault protection |
| Load management | Must be considered where multiple charging points share a single distribution board |
| Continuous duty | The circuit must be rated for continuous duty as the load may be sustained for hours |
Other Notable Sections
| Section | Location | Key Requirements |
|---|---|---|
| Section 709 | Marinas | Specific arrangements for supplies to vessels, including individual RCD protection for each vessel connection |
| Section 710 — Group 0 | Medical locations (general hospital areas) | No applied parts |
| Section 710 — Group 1 | Medical locations (hospital wards) | Applied parts but not vital |
| Section 710 — Group 2 | Medical locations (operating theatres) | Vital applied parts — require IT systems for certain circuits and insulation monitoring devices |
Important Regulation Numbers
| Regulation | Requirement |
|---|---|
| 701.411.3.3 | RCD protection not exceeding 30mA required for all circuits in locations containing a bath or shower |
| 701.415.2 | Conditions under which supplementary bonding may be omitted in bathrooms |
| 701.512.3 | Requirements for wiring systems in zones of bathrooms |
| 702.410.3.4.1 | SELV voltage limits in swimming pool zones |
| 704.410.3.10 | Reduced low voltage requirements for construction sites |
| 705.422.6 | Fire protection measures in agricultural premises |
| 712.411.3.2.1 | Requirements for isolation of PV arrays |
| 722.531.3.101 | RCD requirements for EV charging circuits |
Common Exam Topics
- Bathroom zone dimensions and the IP ratings required in each zone
- Maximum SELV voltage permitted in Zone 0 of a bathroom or swimming pool (12V AC)
- Construction site voltage requirements — 110V centre-tapped to earth (55V to earth)
- EV charging RCD type — Type A vs Type B and when each is required
- Which special locations require supplementary bonding and when it can be omitted
- PV labelling requirements and the inability to isolate a PV array from its energy source during daylight
- The principle that Part 7 supplements (not replaces) the general rules
Study Tips
- Memorise the zone dimensions for bathrooms (701) and swimming pools (702). Draw diagrams to reinforce the spatial relationships between zones.
- Learn the IP rating requirements for each zone. Remember that IPX7 applies to Zone 0 (immersion protection) and IPX4 applies to Zones 1 and 2 (splash protection).
- For construction sites, remember the key voltage: 110V centre-tapped to earth providing 55V to earth for portable tools.
- Understand the difference between Type A and Type B RCDs in the context of EV charging and when each is required.
- Do not try to memorise every regulation number across all special locations. Focus on the sections most frequently tested: 701, 702, 704, 712, and 722.
- Always remember that Part 7 requirements are additional to the general rules. The general requirements still apply in every special location.
Related Topics
Practice Questions: Part 7 - Special Installations or Locations
Test your knowledge with 12 free practice questions. Get all 155 questions in the app.
Question 1 of 12
Part 7 - Special Installations or Locations
Quiz Complete!
0
Correct
0
Incorrect
0%
Score
Get your results emailed to you
Results sent! Check your inbox.
Related Articles
Special Locations in BS 7671: Bathrooms, Swimming Pools, and More
A guide to Part 7 of BS 7671 — bathrooms, swimming pools, saunas, and construction sites, with the zoning rules and RCD requirements for the exam.
Installing a PIR Sensor to an Outside Light: Wiring, IP Ratings & BS 7671 Requirements
A practical guide to wiring a PIR motion sensor to an outdoor light — terminal connections, IP ratings, override switches, and the BS 7671 regs.
Guide to Part 7: Special Installations and Locations
Everything you need to know about Part 7 of BS 7671 covering special installations including bathrooms, swimming pools, construction sites, and more.